3150-SEA

Does this module support any other devices?

Specifically we are trying to replace/upgrade from a SieServe DDE Server without using the Siemens WinPM software since we already have an HMI. There is an existing SLC rack in the substation we are monitoring. Would like to use the Prosoft Module but need support for existing SCOR relays and 4700 power monitors. From the documentation that I have seen, the SCOR is not supported.

Thanks in advance.
Dan Thune, MCSE
Systems Engineer
Control Application and Maintenance, Inc.
dthune@cam-co.org

Tuesday 19 April 2005 2:40:10 am

RE:3150-SEA

The 3100/3150-SEA module supports the SEABUS Plus protocol on Power Meter Models 4300, 4700, and Static Trip III only. Other SEABUS Plus devices that respond like one of these three might also be supported, if those devices' response messages are the same as one of the model listed above. This implementation of the SEABUS Plus protocol supports only read commands, Short or Long Data Reads for the 4700 or Static Trip IIIs; or 4300-type Data Reads.

For additional details on the module, commands and responses expected, please download the User's Manual from the following website:
http://216.152.245.92/content/view/full/1150.

SCOR relays are not specifically listed as a supported device; but, if they respond to Data Reads in a format like one of the listed devices, they may work. If you determine this is a possiblilty, you might want to ask for a 3150-SEA on the "Try Before You Buy" program to test it for your application before you actually purchase it.