merlinknight

Friday 06 May 2005 1:22:37 am

mvi156-MNET

I have a Bently Nevada that i have to talk through a MNEt module in a controllogix AB PLC. The ethernet cable from the MNET card card goes through a switching hub then to the Bently 3500.
I also have a ABB DCS system that talks modbus that is also connected to this hub.
I take it i have to talk to the Bently using port 2000 because the bently 3500/92 com gateway card protocol is ( Etherner tcp/ip frame and modbus/tcp) or is this protocol the regular modbus tcp/ip an i use port 502?
Also how would i get the ABB DCS (set as MASTER) system to talk to the MNET card to get the modbus data at add 40000 from the module? Does the module need to be configure as Server or Client?
I take it that the ABB DCS needs to talk on port 500 because it is normal tcpip modbus?
Lost at the moment. I understand the ControlLogix ladder rung info just don't know how to configure the MNET module.
Any help would greatly be appreciated or atleast a direction to go.

Thanks

jsanders

Friday 06 May 2005 2:50:01 am

RE:mvi156-MNET

The on-line manual for the Bently Nevada 3500/92 comm module says it is capable of Modbus communication via serial port or Modbus TCP communication via Ethernet. It does not specify what Service port to use for Modbus TCP.

The ProSoft MVI56-MNET Client is capable of creating Modbus TCP commands to access data from either Service 502 (standard Modbus TCP) or Service Port 2000 (Encapsulated Modbus Serial RTU over Ethernet.) You will need to contact Bently Nevada Tech Support to find out which service port to use for their equipment; but it will probably be 502 for straight Modbus TCP.

As for the ABB DCS, I assume you mean that it also talks Modbus TCP, since you have it connected through the Ethernet hub. As a Modbus TCP Server to the ABB DCS Client, the MVI56-MNET will respond to commands sent to the module's IP address using Service Port 502, not 500. To read or write internal module memory address 0 as a 16-bit register value, use FC 3, address 40001 in your DCS poll command.

In our MVI56-MNET module, internal memory addresses 0-3999 are made available by our Modbus TCP Server driver as virtual Modbus bit addresses 00001-63999 for bit Function Codes (FCs) 1, 5, or 15 [note: addressing for bit commands is done by bit number, not register address]; as Input Register addresses 30001-34000 for Input Register FC 4; and as Holding Register addresses 40001-44000 for Holding Register FC 3, 6 or 16; assuming you leave all the Offset values set to zero in your MNET configuration file. In other words, data for bit addresses 00001-00016, register 30001, and register 40001 will all come from the same internal module memory address of 0, unless you use Offset values to change the default starting points of the different register address ranges (default is 0.)

If you need a more detailed explanation, you may want to call Prosoft Tech Support at: (661) 716-5100.