Tuesday 26 July 2005 11:06:53 am |
|
|
MVI46-ACF Resettable accumulators
I wish to be able to read the value of the resettable accumulators from the M registers for each of the meters. I am currently able to read the non resettable accumulators but not the resettable ones. I need the M register address for them.
|
|
jsanders
|
Thursday 17 November 2005 8:59:04 am |
|
|
RE:MVI46-ACF Resettable accumulators
There are no direct M register addresses for reading the Resettable Accumulators in the MVI46-AFC module. To read these accumulators, you will need to consult the Modbus Map for the module and then use the Modbus Gateway function of the ladder logic to read the Modbus addresses associated with those accumulators.
|