MVI46-MCM
You need to be logged in to get access to the forums. You can do so here
|
sibym2000
|
Friday 14 July 2006 11:45:00 pm |
|
|
MVI46-MCM
i have an MCm module configured and on my master port (Port 1) i can read datas on the N31:0 registers from M1:1.200 being written thru Modbus simulator (Modsim),but i cant see the datas written in to the N32 registers at location M1:1.0 Registers at the Modbus Simulator .I have not used any offsets( N10-MCM Cmds). I am trying to manipulate the Ladder which came along with the module.Any comments and help is highly appreciated
|
|
jsanders
|
Monday 17 July 2006 11:22:43 am |
|
|
RE:MVI46-MCM
If one type of command is working, there is no reason to expect a different command would not work. When I have encountered this problem in the past, it has been an issue of how the Simulator address range was configured. Please be sure you are looking at the correct address range for each type of command. And check the Internal Addresses and Device Addresses in your Write Commands, to be sure the data is coming from Internal Addresses from 0 -199 and that your commands are sending that data to the address range you are displaying in your simulator program.
|