MVI56-MNET configuration file


You need to be logged in to get access to the forums. You can do so here

cbehr

Sunday 12 December 2004 11:14:04 pm

MVI56-MNET configuration file

What is MBAP (port 502) and MNET (port 2000) and which do I use for communication on modbus over TCP/IP

CH

Monday 13 December 2004 12:11:02 pm

RE:MVI56-MNET configuration file

The majority of Modbus TCP devices use port 502. Some devices, like serial to Ethernet converters, can place serial data from a Modbus RTU device on an Ethernet network (encapsulated serial). This is when you would use Port 2000.

ProSoft Support Team

Monday 13 December 2004 12:11:26 pm

RE:MVI56-MNET configuration file

MBAP (port 502) is what most people refer to as ModbusTCP/IP.

Port 2000 will produce a standard Modbus RTU packet, including CRC, wrapped in a TCP/IP wrapper. With Port 2000 calls, a TCP/IP device can strip off the TCP/IP wrapper, and then pass the resulting Modbus RTU packet to a serial Modbus device.