Wednesday 25 January 2006 2:26:33 am

1 Slave Radio(6105-WA-PDPS), 3 Master Radios(6104-WA-PDPM)

Here is the current configuration of my network:

-Siemens PLC is connected with the 6105-WA-PDPS.
-The 6105-WA-PDPS is talking WIRELESSLY with three 6104-WA-PDPMs.
-Each 6104-WA-PDPM is connected with a drive.

Right now, this set up works great. Communication is running fine.
My question is:
-Is there any way that the PLC knows when one of the masters radio lost connection with the slave radio? or is the Slave radio knows when one of the masters radio not communicating anymore?

Thanks

gary

Wednesday 01 February 2006 1:47:28 pm

RE:1 Slave Radio(6105-WA-PDPS), 3 Master Radios(6104-WA-PDPM)

This is the bit she can use to determine the communication status with the master’s and it’s (all) slaves.

I changed the bit order to:
With this register they can look at bit 0 and bit 1 as follows:


Bit Bit

1 0 Condition

0 0 Waiting for Initialization

0 1 Initialized and ready to run or running

1 X Master not in run or ready mode (register is set to 0XFFFF)


So if bit 1 is set there is a problem with the master.