5102-DFS3-DFM

I am having no luck communicating from my A/B slc channel 0 to the master port on my 5102. I have gone through the set up and download and matched channel 0 to the master port. I have an rs422 device working on port 0 and an rs232 device working on port 1. Any ideas on what could be causing this?

jsanders

Tuesday 12 July 2005 8:58:52 am

RE:5102-DFS3-DFM

This module is only designed to allow multiple DF-1 Masters to talk to one PLC/SLC Channel 0 port when it is configured as a DF-1 Slave. If you are trying to use the PLC/SLC as a DF-1 Master and multiplex it to multiple Slaves through our module, this will not work. You would need the 5102-MCM4_DFCM for that application.

To diagnose problems of this nature, we will need to see a copy of the configuration file you are using for the module as well as the ladder logic for the PLC you are using as your DF-1 Slave.

Please send the files to: support@psft.com and we will be happy to look at them and make suggestions on how to get your multiple Masters communicating to the Slave PLC through our module.